Fault 30027 = Power unit Precharging DC link time monitoring is exceeded. Please check the input AC voltage, 3 phase balance value, line contcator & its correct operation.
Please check the fault value in r0949 (interpret it in binary from Hex) & report it here.
Dear PISCEAN,
I have the same problem (F30027) with r949 fault value bit 8 (655098).
whats the problem,
Power supply is OK (415VAC, 50Hz)
DC link voltage 2.2V
Best Regards
------------------------------------------------------------------------------------------
Split from
30027 fault
.
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!