SINAMICS general: F30027

PISCEAN 2010
Hello,
Fault 30027 = Power unit Precharging DC link time monitoring is exceeded. Please check the input AC voltage, 3 phase balance value, line contcator & its correct operation.
Please check the fault value in r0949 (interpret it in binary from Hex) & report it here.
 Dear PISCEAN,
I have the same problem (F30027) with r949 fault value bit 8 (655098).
whats the problem,
Power supply is OK (415VAC, 50Hz)
DC link voltage 2.2V
Best Regards
------------------------------------------------------------------------------------------