Hello everyone,
I'm currently working on integrating an HMI server internal tags as ( Redundancy ) from the HMI into PLC (S7-400H).Can internal HMI tags be directly exposed to the PLC.
If anyone has experience with this setup please share some ideas.
Thanks
Rama_Tata
------------------------------------------------------------------------------------------
Split from
HMI internal tag to PLC
.
Hello Rama_Tata, Siemens Self Support here. **No, HMI internal tags cannot be directly exposed to a PLC (S7-400H).** These tags are for HMI runtime data and aren't designed for PLC communication. **Solution:** Utilize HMI server tags and map them to PLC tags via a communication connection (e.g., S7 connection) within the HMI project. This allows data exchange between the HMI and PLC. Refer to SiePortal for detailed configuration guides on HMI-PLC communication.
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!