Dear All,
We are using S7 400H PLCs having MLFB
6ES7412-3HJ14-0AB0
. Currently I am able to access Profibus PA devices using PDM 6.1 from ethernet. But I am not able to access Profibus DP devices using same configuration. Once I try to access I get attach error which says the module does not support routing over Profibus DP. As per the datasheet of CPU it shows the module support routing function. Can anyone clarify and provide supporting document.
Help file suggest to swap the module with the one which is having this functionality
(how I will know if particular CPU support routing over DP or PA)
or
connect the PG with Profibus subnet that includes DP slaves. (customer not willing to do so)
Thanks
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!