YES! The LOGO! 12/24RC(o), 24RC(o) and 230RC(o) all have
potential-free
RELAY outputs.
The LOGO! program only closes the relay.
You can supply one side of the Q1 relay with an AC voltage like 220V and this will be connected to the rest of the circuit when the relay is closed.
On Q2, you could put 12V DC on one side of the relay and this will be provided to the rest of the connected circuit when the LOGO! program closes the digital relay.
You can do this for all relay outputs of the LOGO!, even on the expnasion modules (but then only 5A current limit)
For AC current through these relay (on the main LOGO! unit), the relays can handle 10A of current.
For DC current through the relays, I would suggest not going above 8A - this will make the life of the relays longer.
Cheers
Aaaaarrrggghhhh!!!!! ("Have a nice day!")
hi barbarian ,
one more thing about outputs , is it same for s7-200 cpu 224 relay output .
Splitted from
logo outputs
.
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!