Good afternoon!
I hope all of you be ok.
I have a very strange situation in a customer plant, and I would like if someone could help me.
Customer has a S7-300 PLC connected by ProfiBus to an et200M which has 3 DI modules and 3 DO modules put in this way:
PS -- ET200M – DI (1) – DI(2) – DI(3) – DO(4) – DO(5) – DO(6)
Problem:
The input signals of DI (2) arrive to the PLC with a delay of 20 seconds, but in the other modules the signals arrive to the PLC in a properly time. I checked this by STEP7 – VAR TAB
I performed the following tests:
Electrical installation: OK
Environmental conditions: OK
Machine vibrations: NO OK (I detected moderate vibration)
Solution:
Firstly, I changed the DI (2) module by a new one, but the delay persists.
Secondly, I returned the old module to DI (2) position and changed DI (1) by the new one and PUFF! The delay in the DI (2) disappeared.
Did someone have a similar situation? Can someone try to explain this issue?
Sorry for my English!
Thanks in advance!
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!