Logo8 programmed as a thermostat:
start 28 ° C stop 26 ° C
however, it starts at 28.5 ° C and stops at 26.3 ° C.
How come?
And is it not possible to give a start at 26.5 ° instead of just round numbers?
With thanks
Greetings Fernando
Dear Fernando,
The slight deviation you're observing (starting at 28.5°C instead of 28°C, stopping at 26.3°C instead of 26°C) is due to the inherent analog-to-digital conversion and resolution of the temperature sensor and the LOGO! 8's processing.
The LOGO! 8 doesn't work with infinitely precise temperature readings. It samples the analog signal and converts it to a digital value. This introduces a small amount of error. Also, the display resolution might show one decimal place while the internal comparison uses a different precision.
Regarding using decimal start values like 26.5°C: Yes, it is possible. You can directly input decimal values in the LOGO!Soft Comfort program for your temperature setpoints. There are no restrictions to only using whole numbers.
For more detailed information on LOGO! 8 analog input handling, please refer to the SiePortal documentation:
Sincerely,
Siemens Self Support
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!